    EATON AMA

    Scheduled Pinned Locked Moved IT Discussion
    eatonama
    208 Posts 25 Posters 126.1k Views
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • scottalanmillerS
      scottalanmiller
      last edited by

      Server Current is the force of the flowing servers in the computational stream.

      art_of_shredA dafyreD 2 Replies Last reply Reply Quote 0
      • windsoW
        windso Vendor @dafyre
        last edited by

        @dafyre , good point, I edit the wording. See above. Really I mean current on each phase. Poorly worded. Sorry!

        1 Reply Last reply Reply Quote 1
        • art_of_shredA
          art_of_shred @scottalanmiller
          last edited by

          @scottalanmiller said:

          Server Current is the force of the flowing servers in the computational stream.

          Don't try to answer electrical questions with IT answers. lol

          1 Reply Last reply Reply Quote 3
          • dafyreD
            dafyre @scottalanmiller
            last edited by

            @scottalanmiller ❓ 💥 ❓ -- Mind = Blown

            1 Reply Last reply Reply Quote 2
            • JColeKenJ
              JColeKen Vendor @dafyre
              last edited by

              @dafyre Cha-ching!

              1 Reply Last reply Reply Quote 0
              • JColeKenJ
                JColeKen Vendor @art_of_shred
                last edited by

                @art_of_shred Actual operating load is the most practical.

                coliverC art_of_shredA 2 Replies Last reply Reply Quote 0
                • coliverC
                  coliver @JColeKen
                  last edited by

                  @JColeKen said:

                  @art_of_shred Actual operating load is the most practical.

                  How would you measure this in an environment without power monitoring? Or is it basically a guess at that point?

                  art_of_shredA 1 Reply Last reply Reply Quote 0
                  • art_of_shredA
                    art_of_shred @JColeKen
                    last edited by

                    @JColeKen said:

                    @art_of_shred Actual operating load is the most practical.

                    Is there a simple percentage to use there as a ballpark figure?

                    JColeKenJ 1 Reply Last reply Reply Quote 0
                    • art_of_shredA
                      art_of_shred @coliver
                      last edited by

                      @coliver said:

                      @JColeKen said:

                      @art_of_shred Actual operating load is the most practical.

                      How would you measure this in an environment without power monitoring? Or is it basically a guess at that point?

                      An ammeter works great if you have one and want real numbers.

                      scottalanmillerS windsoW 2 Replies Last reply Reply Quote 1
                      • JColeKenJ
                        JColeKen Vendor @art_of_shred
                        last edited by

                        @art_of_shred 70-80% is a safe bet. Sometimes it is lower, but that is typically what I default to when sizing.

                        1 Reply Last reply Reply Quote 2
                        • scottalanmillerS
                          scottalanmiller @art_of_shred
                          last edited by

                          @art_of_shred said:

                          @coliver said:

                          @JColeKen said:

                          @art_of_shred Actual operating load is the most practical.

                          How would you measure this in an environment without power monitoring? Or is it basically a guess at that point?

                          An ammeter works great if you have one and want real numbers.

                          Even in the afternoon or do you have to switch to a PMmeter?

                          JColeKenJ art_of_shredA 2 Replies Last reply Reply Quote 1
                          • windsoW
                            windso Vendor @art_of_shred
                            last edited by windso

                            @art_of_shred @coliver

                            Yes! These can be somewhat inexpensive. We usually see IT equipment running at 60% or less of nameplate rating. The challenge we have when sizing a UPS or PDU, and you will have too, is that generic rules always bite you at some point. If you are the exception, you risk taking down everything.

                            Keep in mind that sizing a UPS or PDU at less than 80% or 100% utilization is a good thing. UPSs and PDUs are like the breakers feeding your Christmas tree lights - Once you add too much, the lights go off!

                            art_of_shredA 1 Reply Last reply Reply Quote 3
                            • JColeKenJ
                              JColeKen Vendor @scottalanmiller
                              last edited by

                              @scottalanmiller Lolz

                              1 Reply Last reply Reply Quote 1
                              • art_of_shredA
                                art_of_shred @scottalanmiller
                                last edited by

                                @scottalanmiller said:

                                @art_of_shred said:

                                @coliver said:

                                @JColeKen said:

                                @art_of_shred Actual operating load is the most practical.

                                How would you measure this in an environment without power monitoring? Or is it basically a guess at that point?

                                An ammeter works great if you have one and want real numbers.

                                Even in the afternoon or do you have to switch to a PMmeter?

                                Once again sporting your prowess in all things electrical. I defer to your expertise...

                                1 Reply Last reply Reply Quote 1
                                • NicN
                                  Nic
                                  last edited by

                                  Couple of ones that might be more home oriented than business:

                                  1. Do you have any plans to get into the home battery market, like Tesla? (or are you already) These are the backup batteries that you can charge from solar and then power your home from (or use as a backup for if the power is out).
                                  2. What would you recommend in the prosumer market for IT pros or technically minded folks to use at home?
                                  windsoW 1 Reply Last reply Reply Quote 4
                                  • art_of_shredA
                                    art_of_shred @windso
                                    last edited by

                                    @windso said:

                                    @art_of_shred @coliver

                                    Yes! These can be somewhat inexpensive. We usually see loads running at 60% or less of nameplate rating. The challenge we have, and you will have too, is that generic rules always bite you at some point. If you are the exception, you risk taking down everything.

                                    Keep in mind that sizing a circuit at less than 80% or 100% is a good thing. You never want to completely oversize, but UPSs and PDUs are like the breakers feeding your Christmas tree lights - Once you add too much, the lights go off!

                                    Just to clarify, I thought that was worded a little confusingly. You never want your load to equal or surpass your protection. Ideally, your expected amp load should only be about 80% of your protection's full capacity. Otherwise, you can exceed its ability to protect and either diminish its performance or nullify the protection altogether.

                                    windsoW 1 Reply Last reply Reply Quote 2
                                    • art_of_shredA
                                      art_of_shred
                                      last edited by

                                      That didn't sound good when I read it, so keep your mind out of the gutter.

                                      scottalanmillerS 1 Reply Last reply Reply Quote 0
                                      • scottalanmillerS
                                        scottalanmiller @art_of_shred
                                        last edited by

                                        @art_of_shred said:

                                        That didn't sound good when I read it, so keep your mind out of the gutter.

                                        Too late.

                                        1 Reply Last reply Reply Quote 0
                                        • dafyreD
                                          dafyre
                                          last edited by

                                          Are any of your PDUs capable of being remotely managed? So we can power stuff on / off remotely?

                                          mdecampM 1 Reply Last reply Reply Quote 2
                                          • J
                                            Jason Banned
                                            last edited by

                                            Do you offer and trade in discounts for large UPSs to switch to Eaton? We currently have Liebert 3 Phase UPS systems.