      Doing some back reading on UPS units, I'm looking at a Eaton unit for a small SMB with about 15 users.

      Preferences is for a Rack Mount unit that can support the following equipment:

      • FIOS router
      • UBNT Router
      • UBNT 24 PoE router
      • Dell PE 610
      • Lenovo NAS

      Right now I'm leaning towards the Eaton 5PX 1500
      0_1449084827161_5PX-RT-2U-1500-sku[1].jpg

      coliverC 1 Reply Last reply Reply Quote 0
      • coliverC
        coliver @gjacobse
        last edited by

        @gjacobse said:

        Doing some back reading on UPS units, I'm looking at a Eaton unit for a small SMB with about 15 users.

        Preferences is for a Rack Mount unit that can support the following equipment:

        • FIOS router
        • UBNT Router
        • UBNT 24 PoE router
        • Dell PE 610
        • Lenovo NAS

        Right now I'm leaning towards the Eaton 5PX 1500
        0_1449084827161_5PX-RT-2U-1500-sku[1].jpg

        I had two of these at my last position and had no real issues. I forgot to get the networking module though so that was one downside.

        1 Reply Last reply Reply Quote 1
        • gjacobseG
          gjacobse
          last edited by

          As the PE610 has dual PSU, is it a must that both need to be in a UPS,.. You never want to have both in the same UPS.

          scottalanmillerS 1 Reply Last reply Reply Quote 1
          • scottalanmillerS
            scottalanmiller @gjacobse
            last edited by

            @gjacobse said:

            As the PE610 has dual PSU, is it a must that both need to be in a UPS,.. You never want to have both in the same UPS.

            Dual PSU should ideally have each PSU going into an independent UPS unit.

            1 Reply Last reply Reply Quote 1
            • gjacobseG
              gjacobse
              last edited by

              Ideally,.. I fully agree.

              But if the site refuse a second unit....

              JaredBuschJ 1 Reply Last reply Reply Quote 1
              • JaredBuschJ
                JaredBusch @gjacobse
                last edited by

                @gjacobse said:

                Ideally,.. I fully agree.

                But if the site refuse a second unit....

                Then tell them that they are killing their battery time trying to save $200

                Plugging both into the same UPS will just drain faster. Also plugging one into power and not a UPS will cause it to drain faster because the system will kick the one powered PSU into a higher consumption mode when it detects a failure on the other.

                Either way a significant drain on the UPS battery.

                1 Reply Last reply Reply Quote 2
                • scottalanmillerS
                  scottalanmiller
                  last edited by

                  And it is more than just drain, it is partially defeating the purpose of the second PSU. It's like having two NICs bonded on your server but only having one switch to plug them into. Sure, it is better than nothing, but it is not delivering the redundancy that you hope for or pay for. If anything goes wrong with that one UPS the redundant PSUs will be useless.

                  1 Reply Last reply Reply Quote 1