    Pi as a UPS monitor

    IT Discussion
    raspberry pi ups apc eaton nut
    8
    114
    33.9k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • JaredBuschJ
      JaredBusch
      last edited by

      Alright, I plugged the thing back in and got to testing.

      Yeah! It still communicates.

      pi@raspberrypi:~ $ sudo upsc jaredoffice
      Init SSL without certificate database
      battery.charge: 84
      battery.charge.low: 10
      battery.charge.warning: 50
      battery.date: 2001/09/25
      battery.mfr.date: 2010/12/15
      battery.runtime: 1236
      battery.runtime.low: 120
      battery.type: PbAc
      battery.voltage: 27.0
      battery.voltage.nominal: 24.0
      device.mfr: American Power Conversion
      device.model: Back-UPS BR1000G
      device.serial: 3B1051X20329
      device.type: ups
      driver.name: usbhid-ups
      driver.parameter.pollfreq: 30
      driver.parameter.pollinterval: 2
      driver.parameter.port: auto
      driver.version: 2.7.2
      driver.version.data: APC HID 0.95
      driver.version.internal: 0.38
      input.sensitivity: medium
      input.transfer.high: 147
      input.transfer.low: 88
      input.transfer.reason: input voltage out of range
      input.voltage: 124.0
      input.voltage.nominal: 120
      ups.beeper.status: enabled
      ups.delay.shutdown: 20
      ups.firmware: 868.L1 .D
      ups.firmware.aux: L1
      ups.load: 20
      ups.mfr: American Power Conversion
      ups.mfr.date: 2010/12/15
      ups.model: Back-UPS BR1000G
      ups.productid: 0002
      ups.realpower.nominal: 600
      ups.serial: 3B1051X20329
      ups.status: OL CHRG
      ups.test.result: No test initiated
      ups.timer.reboot: 0
      ups.timer.shutdown: -1
      ups.vendorid: 051d
      
      1 Reply Last reply Reply Quote 3
      • JaredBuschJ
        JaredBusch
        last edited by JaredBusch

        Pulled the power cord from the wall. UPS beeps, but nothing from nut.

        Ok back to the manual and checking the conf files.

        Well it would probably help if I told the thing what to monitor..
        /etc/nut/upsmon.conf

        MONITOR jaredoffice@localhost 1 upsmon demo master
        

        Oh but those details have to match /etc/nut/ups.conf and /etc/nut/upsd.users. Well I already know that my unit is called jaredoffice@localhost from ups.conf. So just edit upsd.users.

        pi@raspberrypi:~ $ sudo nano /etc/nut/upsd.users
        # put at end of file
        [upsmon]
        password = demo
        upsmon master
        

        Now reload the monitor

        pi@raspberrypi:~ $ sudo upsmon -c reload
        Network UPS Tools upsmon 2.7.2
        pi@raspberrypi:~ $
        

        Then unplug the UPS. and get nothing.

        look in the logs..
        tail/var/log/syslog

        Feb  1 17:05:38 raspberrypi upsmon[732]: UPS jaredoffice@localhost on battery
        Feb  1 17:05:38 raspberrypi rsyslogd-2007: action 'action 17' suspended, next retry is Wed Feb  1 17:06:08 2017 [try http://www.rsyslog.com/e/2007 ]
        Feb  1 17:05:38 raspberrypi upssched[964]: Can't open /etc/nut/upssched.conf: Permission denied
        Feb  1 17:05:48 raspberrypi upsmon[732]: UPS jaredoffice@localhost on line power
        Feb  1 17:05:48 raspberrypi upssched[967]: Can't open /etc/nut/upssched.conf: Permission denied
        

        Say to yourself, WTF did I do 3 months ago....

        Time to reload and start over.

        gjacobseG 1 Reply Last reply Reply Quote 0
        • gjacobseG
          gjacobse @JaredBusch
          last edited by

          @JaredBusch said in Pi as a UPS monitor:

          Pulled the power cord from the wall. UPS beeps, but nothing from nut.

          Ok back to the manual and checking the conf files.

          Well it would probably help if I told the thing what to monitor..
          /etc/nut/upsmon.conf

          MONITOR jaredoffice@localhost 1 upsmon demo master
          

          Oh but those details have to match /etc/nut/ups.conf and /etc/nut/upsd.users. Well I already know that my unit is called jaredoffice@localhost from ups.conf. So just edit upsd.users.

          pi@raspberrypi:~ $ sudo nano /etc/nut/upsd.users
          # put at end of file
          [upsmon]
          password = demo
          upsmon master
          

          Now reload the monitor

          pi@raspberrypi:~ $ sudo upsmon -c reload
          Network UPS Tools upsmon 2.7.2
          pi@raspberrypi:~ $
          

          Then unplug the UPS. and get nothing.

          look in the logs..
          tail/var/log/syslog

          Feb  1 17:05:38 raspberrypi upsmon[732]: UPS jaredoffice@localhost on battery
          Feb  1 17:05:38 raspberrypi rsyslogd-2007: action 'action 17' suspended, next retry is Wed Feb  1 17:06:08 2017 [try http://www.rsyslog.com/e/2007 ]
          Feb  1 17:05:38 raspberrypi upssched[964]: Can't open /etc/nut/upssched.conf: Permission denied
          Feb  1 17:05:48 raspberrypi upsmon[732]: UPS jaredoffice@localhost on line power
          Feb  1 17:05:48 raspberrypi upssched[967]: Can't open /etc/nut/upssched.conf: Permission denied
          

          Say to yourself, WTF did I do 3 months ago....

          Time to reload and start over.

          think i got the same thing, and decide the same course of action, to which I have not moved forward with. Albeit, it's not on a rPi but a desktop - premise is the same.

          Think we may have to create a user for the NUT system.... but again,.. can't work with it right now.

          1 Reply Last reply Reply Quote 0
          • JaredBuschJ
            JaredBusch
            last edited by JaredBusch

            Quick check of upsmon.conf found this, uncommented it.

            # RUN_AS_USER nut
            

            Rebooted Pi, unplugged UPS.

            Broadcast message from nut@raspberrypi (somewhere) (Wed Feb  1 17:19:04 2017):
            
            UPS jaredoffice@localhost on battery
            
            
            Broadcast message from nut@raspberrypi (somewhere) (Wed Feb  1 17:19:24 2017):
            
            UPS jaredoffice@localhost on line power
            
            1 Reply Last reply Reply Quote 0
            • JaredBuschJ
              JaredBusch
              last edited by

              Syslog had this though.

              Feb  1 17:19:04 raspberrypi upsmon[734]: UPS jaredoffice@localhost on battery
              Feb  1 17:19:11 raspberrypi upssched[792]: Failed to connect to parent and failed to create parent: No such file or directory
              Feb  1 17:19:24 raspberrypi upsmon[734]: UPS jaredoffice@localhost on line power
              

              Back to the config files we go!
              /etc/nut/upssched.conf

              # PIPEFN <filename>
              # This is commented out by default to make you visit this file and think
              # about how your system works before potentially opening a hole.
              

              FFS, but it gets better! Right below that, also commented out.

              # LOCKFN <filename>
              #
              # REQUIRED.  This was added after version 1.2.1.
              #
              # upssched needs to be able to create this filename in order to avoid
              # a race condition when two events are dispatched from upsmon at nearly
              # the same time.  This file will only exist briefly.  It must not be
              # created by any other process.
              #
              # You should put this in the same directory as PIPEFN.
              #
              

              So I update the config and make a directory forgetting to chown it from root /sigh...

              PIPEFN /etc/nut/upssched/upssched.pipe
              LOCKFN /etc/nut/upssched/upssched.lock
              1 Reply Last reply Reply Quote 0
              • JaredBuschJ
                JaredBusch
                last edited by JaredBusch

                Once it was all chowned...

                Feb  1 17:33:08 raspberrypi upssched[793]: Timer daemon started
                Feb  1 17:33:09 raspberrypi upssched[793]: New timer: onbattwarn (30 seconds)
                Feb  1 17:33:39 raspberrypi upssched[793]: Event: onbattwarn
                Feb  1 17:33:54 raspberrypi upssched[793]: Timer queue empty, exiting
                

                And output to the screen:

                Broadcast message from nut@raspberrypi (somewhere) (Wed Feb  1 17:33:39 2017):
                
                The UPS is currently running on battery power!
                
                1 Reply Last reply Reply Quote 0
                • JaredBuschJ
                  JaredBusch
                  last edited by

                  Now time to wipe, replicate, test and document.

                  Then the command can be changed to send email.

                  1 Reply Last reply Reply Quote 3
                  • JaredBuschJ
                    JaredBusch
                    last edited by JaredBusch

                    Following my own notes from post 62
                    At step 11 (installing nut form repo) I see an error.
                    May or may not have gotten this the first time around..

                    pi@bna-pwr-pi-01:~ $ sudo apt-get install nut
                    Reading package lists... Done
                    <snip>
                    Unpacking nut (2.7.2-4) ...
                    Processing triggers for man-db (2.7.0.2-5) ...
                    Processing triggers for systemd (215-17+deb8u6) ...
                    Setting up libnspr4:armhf (2:4.12-1+debu8u1) ...
                    Setting up libnss3:armhf (2:3.26-1+debu8u1) ...
                    Setting up libupsclient4:armhf (2.7.2-4) ...
                    Setting up nut-client (2.7.2-4) ...
                    Job for nut-monitor.service failed. See 'systemctl status nut-monitor.service' and 'journalctl -xn' for details.
                    invoke-rc.d: initscript nut-client, action "start" failed.
                    Setting up nut-server (2.7.2-4) ...
                    A dependency job for nut-server.service failed. See 'journalctl -xn' for details.
                    invoke-rc.d: initscript nut-server, action "start" failed.
                    Job for nut-driver.service failed. See 'systemctl status nut-driver.service' and 'journalctl -xn' for details.
                    Setting up nut (2.7.2-4) ...
                    Processing triggers for libc-bin (2.19-18+deb8u7) ...
                    Processing triggers for systemd (215-17+deb8u6) ...
                    pi@bna-pwr-pi-01:~ $ systemctl status nut-monitor
                    ā— nut-monitor.service - Network UPS Tools - power device monitor and shutdown controller
                       Loaded: loaded (/lib/systemd/system/nut-monitor.service; enabled)
                       Active: failed (Result: resources) since Thu 2017-02-02 02:10:27 UTC; 49s ago
                    pi@bna-pwr-pi-01:~ $ 
                    
                    1 Reply Last reply Reply Quote 0
                    • JaredBuschJ
                      JaredBusch
                      last edited by

                      ah here we go, this is normal because not configured.

                      pi@bna-pwr-pi-01:~ $ sudo journalctl -xn
                      -- Logs begin at Fri 2016-11-25 18:24:08 UTC, end at Thu 2017-02-02 02:33:03 UTC. --
                      Feb 02 02:32:47 bna-pwr-pi-01 sudo[23103]: pam_unix(sudo:session): session opened for user root by pi(uid=0)
                      Feb 02 02:32:47 bna-pwr-pi-01 systemd[1]: Starting Network UPS Tools - power device monitor and shutdown controller...
                      -- Subject: Unit nut-monitor.service has begun with start-up
                      -- Defined-By: systemd
                      -- Support: http://lists.freedesktop.org/mailman/listinfo/systemd-devel
                      -- 
                      -- Unit nut-monitor.service has begun starting up.
                      Feb 02 02:32:47 bna-pwr-pi-01 upsmon[23113]: upsmon disabled, please adjust the configuration to your needs
                      Feb 02 02:32:47 bna-pwr-pi-01 upsmon[23113]: Then set MODE to a suitable value in /etc/nut/nut.conf to enable it
                      Feb 02 02:32:47 bna-pwr-pi-01 systemd[1]: PID file /var/run/nut/upsmon.pid not readable (yet?) after start.
                      Feb 02 02:32:47 bna-pwr-pi-01 systemd[1]: Failed to start Network UPS Tools - power device monitor and shutdown controller.
                      -- Subject: Unit nut-monitor.service has failed
                      -- Defined-By: systemd
                      -- Support: http://lists.freedesktop.org/mailman/listinfo/systemd-devel
                      -- 
                      -- Unit nut-monitor.service has failed.
                      -- 
                      -- The result is failed.
                      Feb 02 02:32:47 bna-pwr-pi-01 systemd[1]: Unit nut-monitor.service entered failed state.
                      Feb 02 02:32:48 bna-pwr-pi-01 sudo[23103]: pam_unix(sudo:session): session closed for user root
                      Feb 02 02:33:03 bna-pwr-pi-01 sudo[23121]: pi : TTY=pts/0 ; PWD=/home/pi ; USER=root ; COMMAND=/bin/journalctl -xn
                      Feb 02 02:33:03 bna-pwr-pi-01 sudo[23121]: pam_unix(sudo:session): session opened for user root by pi(uid=0)
                      
                      1 Reply Last reply Reply Quote 1
                      • JaredBuschJ
                        JaredBusch
                        last edited by JaredBusch

                        So on to configuration. Nut has only a few config files you need to deal with.

                        We will go right down the list.

                        pi@bna-pwr-pi-01:~ $ ls -l /etc/nut
                        total 44
                        -rw-r----- 1 root nut  1538 Mar 26  2015 nut.conf
                        -rw-r----- 1 root nut  4572 Mar 26  2015 ups.conf
                        -rw-r----- 1 root nut  4578 Mar 26  2015 upsd.conf
                        -rw-r----- 1 root nut  2131 Mar 26  2015 upsd.users
                        -rw-r----- 1 root nut 15170 Mar 26  2015 upsmon.conf
                        -rw-r----- 1 root nut  3887 Mar 26  2015 upssched.conf
                        
                        1 Reply Last reply Reply Quote 0
                        • JaredBuschJ
                          JaredBusch
                          last edited by

                          First up is nut.conf. There is only a single option to set in this file, but it is important.

                          Assuming you are going to have only one device, or if multiple devices, that they will report in on their own, the simplest configuration is to choose standalone

                          MODE=standalone
                          

                          Here are the various meanings from the conf file.

                          # - none: NUT is not configured, or use the Integrated Power Management, or use
                          #   some external system to startup NUT components. So nothing is to be started.
                          # - standalone: This mode address a local only configuration, with 1 UPS
                          #   protecting the local system. This implies to start the 3 NUT layers (driver,
                          #   upsd and upsmon) and the matching configuration files. This mode can also
                          #   address UPS redundancy.
                          # - netserver: same as for the standalone configuration, but also need
                          #   some more network access controls (firewall, tcp-wrappers) and possibly a
                          #   specific LISTEN directive in upsd.conf.
                          #   Since this MODE is opened to the network, a special care should be applied
                          #   to security concerns.
                          # - netclient: this mode only requires upsmon.
                          
                          1 Reply Last reply Reply Quote 0
                          • JaredBuschJ
                            JaredBusch
                            last edited by

                            Next up is ups.conf, again read the config file for more information, it is fairly thorough.

                            In this case I am going to connect it to the APC unit pictured at the beginning of this thread.

                            [bnajaredrouter]
                            driver = usbhid-ups
                            port = auto
                            desc = "Jared Router UPS"
                            
                            1 Reply Last reply Reply Quote 0
                            • JaredBuschJ
                              JaredBusch
                              last edited by

                              The file upsd.conf does not need modified for a typical standalone setup.

                              1 Reply Last reply Reply Quote 0
                              • JaredBuschJ
                                JaredBusch
                                last edited by

                                The file upsd.users needs modified to have the authentication that upsmon will use added to the end of the file.

                                [bnaupsmon]
                                password = AGoodPassword
                                upsmon master
                                
                                1 Reply Last reply Reply Quote 0
                                • JaredBuschJ
                                  JaredBusch
                                  last edited by

                                  The file upsmon.conf starts to get into the nuts and bolts of setting things up to do things for you.

                                  First up will be to uncomment the run as user setting.

                                  RUN_AS_USER nut
                                  

                                  Next is creating the monitor line to tell it what system to monitor. This uses the settings from ups.conf and upsd.users that you previously configured.

                                  MONITOR bnajaredrouter@localhost 1 bnaupsmon AGoodPassword master
                                  

                                  continuing down the file, the next thing to do is to set notifycmd to point to the upssched program

                                  NOTIFYCMD /sbin/upssched
                                  

                                  The final part of this file is to uncomment all of the notify flags and add the EXEC flag to the ones you want to fire the above upssched application. Leaving WALL in while testing is useful, but pretty pointless later for me since the goal is a remote alert.

                                  NOTIFYFLAG ONLINE       SYSLOG+WALL+EXEC
                                  NOTIFYFLAG ONBATT       SYSLOG+WALL+EXEC
                                  NOTIFYFLAG LOWBATT      SYSLOG+WALL
                                  NOTIFYFLAG FSD          SYSLOG+WALL
                                  NOTIFYFLAG COMMOK       SYSLOG+WALL
                                  NOTIFYFLAG COMMBAD      SYSLOG+WALL
                                  NOTIFYFLAG SHUTDOWN     SYSLOG+WALL
                                  NOTIFYFLAG REPLBATT     SYSLOG+WALL
                                  NOTIFYFLAG NOCOMM       SYSLOG+WALL
                                  NOTIFYFLAG NOPARENT     SYSLOG+WALL
                                  
                                  1 Reply Last reply Reply Quote 0
                                  • JaredBuschJ
                                    JaredBusch
                                    last edited by JaredBusch

                                    If you never set any of the flags to EXEC in the previous section, there is nothing to do here, you can stop. But what would be the point of a remote alerting device that does not alert.

                                    So now we come to the last conf file upssched.conf. This one is a bit more annoying because the developers intentionally chose to ship this broken to 'force' you to set up a file yourself.
                                    By default, PIPEFN and LOCKFN are commented out and point to the /var/run/nut/upssched directory that does not exist.

                                    # PIPEFN /var/run/nut/upssched/upssched.pipe
                                    # LOCKFN /var/run/nut/upssched/upssched.lock
                                    

                                    So we make a directory and the pipe file. You are instructed to not make the lock file in the comments.

                                    sudo mkdir /etc/nut/upssched
                                    sudo chown nut:nut /etc/nut/upssched
                                    sudo touch /etc/nut/upssched/upssched.pipe
                                    sudo chown nut:nut /etc/nut/upssched/upssched.pipe
                                    

                                    Editing this file, note the location the shell script that will be called. This is the default, and there is an example script already there, ready to be modified.

                                    CMDSCRIPT /bin/upssched-cmd
                                    

                                    Uncomment and update the PIPE and LOCK lines.

                                    PIPEFN /etc/nut/upssched/upssched.pipe
                                    LOCKFN /etc/nut/upssched/upssched.lock
                                    

                                    Now comes the part that does work, the AT commads. You will want to read the comments and likely the documentation to make full use of this. But here are a couple examples of AT commands to get you going.
                                    When the unit goes on battery, call the shell script to start a 30 second timer named 'onbattwarn'. When the power comes back online, cancel the timer.

                                    AT ONBATT * START-TIMER onbattwarn 30
                                    AT ONLINE * CANCEL-TIMER onbattwarn
                                    AT ONLINE * EXECUTE ongrid
                                    
                                    1 Reply Last reply Reply Quote 0
                                    • JaredBuschJ
                                      JaredBusch
                                      last edited by

                                      Now the final bit of editing, and the one a lot of you will have to simply copy examples for. Editing the shell script that does the actual work.

                                      You can look at the default script and see that because there was no default AT command with 'upsgone' as an named trigger, nothing would ever happen. Let's make it useful.

                                      sudo nano /bin/upssched-cmd

                                      #! /bin/sh
                                      case $1 in
                                              ongrid)
                                                      logger -t upssched-cmd "The UPS is now on grid power."
                                                      ;;
                                              onbattwarn)
                                                      logger -t upssched-cmd "The UPS has been on battery power for 30 seconds."
                                                      ;;
                                              *)
                                                      logger -t upssched-cmd "Unrecognized command: $1"
                                                      ;;
                                      esac
                                      
                                      1 Reply Last reply Reply Quote 0
                                      • JaredBuschJ
                                        JaredBusch
                                        last edited by

                                        And something is broke, but since I followed the directions I had previously wrote in October, that I means I left out something I did.

                                        pi@bna-pwr-pi-01:/etc/nut $ tail -f /var/log/syslog
                                        Feb  2 04:20:42 bna-pwr-pi-01 systemd[1]: Starting Network UPS Tools - power device monitor and shutdown controller...
                                        Feb  2 04:20:42 bna-pwr-pi-01 upsmon[1284]: fopen /var/run/nut/upsmon.pid: No such file or directory
                                        Feb  2 04:20:42 bna-pwr-pi-01 upsmon[1284]: UPS: bnajaredrouter@localhost (master) (power value 1)
                                        Feb  2 04:20:42 bna-pwr-pi-01 upsmon[1284]: Using power down flag file /etc/killpower
                                        Feb  2 04:20:42 bna-pwr-pi-01 upsmon[1286]: Startup successful
                                        Feb  2 04:20:42 bna-pwr-pi-01 upsmon[1287]: Init SSL without certificate database
                                        Feb  2 04:20:42 bna-pwr-pi-01 systemd[1]: nut-monitor.service: Supervising process 1287 which is not our child. We'll most likely not notice when it exits.
                                        Feb  2 04:20:42 bna-pwr-pi-01 systemd[1]: Started Network UPS Tools - power device monitor and shutdown controller.
                                        Feb  2 04:20:42 bna-pwr-pi-01 upsmon[1287]: UPS [bnajaredrouter@localhost]: connect failed: Connection failure: Connection refused
                                        Feb  2 04:20:42 bna-pwr-pi-01 upsmon[1287]: Communications with UPS bnajaredrouter@localhost lost
                                        Feb  2 04:20:47 bna-pwr-pi-01 upsmon[1287]: UPS [bnajaredrouter@localhost]: connect failed: Connection failure: Connection refused
                                        Feb  2 04:20:47 bna-pwr-pi-01 upsmon[1287]: UPS bnajaredrouter@localhost is unavailable
                                                                                                                       
                                        Broadcast message from nut@bna-pwr-pi-01 (somewhere) (Thu Feb  2 04:20:47 2017)
                                                                                                                       
                                        UPS bnajaredrouter@localhost is unavailable                                    
                                                                                                                       
                                        Feb  2 04:20:52 bna-pwr-pi-01 upsmon[1287]: UPS [bnajaredrouter@localhost]: connect failed: Connection failure: Connection refused
                                        Feb  2 04:20:57 bna-pwr-pi-01 upsmon[1287]: UPS [bnajaredrouter@localhost]: connect failed: Connection failure: Connection refused
                                        Feb  2 04:21:02 bna-pwr-pi-01 upsmon[1287]: UPS [bnajaredrouter@localhost]: connect failed: Connection failure: Connection refused
                                        Feb  2 04:21:07 bna-pwr-pi-01 upsmon[1287]: UPS [bnajaredrouter@localhost]: connect failed: Connection failure: Connection refused
                                        
                                        1 Reply Last reply Reply Quote 0
                                        • JaredBuschJ
                                          JaredBusch
                                          last edited by JaredBusch

                                          Manually executed sudo start upsd and got a driver error. Fixed typo, rebooted, and it is online.

                                          pi@bna-pwr-pi-01:~ $ tail -f /var/log/syslog
                                          Feb  2 04:27:24 bna-pwr-pi-01 systemd[1]: Reached target Graphical Interface.
                                          Feb  2 04:27:24 bna-pwr-pi-01 systemd[1]: Starting Update UTMP about System Runlevel Changes...
                                          Feb  2 04:27:24 bna-pwr-pi-01 upsmon[737]: Init SSL without certificate database
                                          Feb  2 04:27:24 bna-pwr-pi-01 systemd[1]: Started Update UTMP about System Runlevel Changes.
                                          Feb  2 04:27:24 bna-pwr-pi-01 systemd[1]: Startup finished in 2.052s (kernel) + 10.336s (userspace) = 12.389s.
                                          Feb  2 04:27:24 bna-pwr-pi-01 upsd[733]: User bnaupsmon@::1 logged into UPS [bnajaredrouter]
                                          Feb  2 04:27:31 bna-pwr-pi-01 dhcpcd[698]: wlan0: no IPv6 Routers available
                                          Feb  2 04:27:51 bna-pwr-pi-01 systemd[1]: Time has been changed
                                          Feb  2 04:27:52 bna-pwr-pi-01 upsd[733]: Data for UPS [bnajaredrouter] is stale - check driver
                                          Feb  2 04:27:52 bna-pwr-pi-01 upsd[733]: UPS [bnajaredrouter] data is no longer stale
                                          
                                          pi@bna-pwr-pi-01:~ $ sudo upsc bnajaredrouter
                                          Init SSL without certificate database
                                          battery.charge: 100
                                          battery.charge.low: 10
                                          battery.charge.warning: 50
                                          battery.date: 2001/09/25
                                          battery.mfr.date: 2010/12/15
                                          battery.runtime: 14100
                                          battery.runtime.low: 120
                                          battery.type: PbAc
                                          battery.voltage: 27.3
                                          battery.voltage.nominal: 24.0
                                          device.mfr: American Power Conversion
                                          device.model: Back-UPS BR1000G
                                          device.serial: 3B1051X20349  
                                          device.type: ups
                                          driver.name: usbhid-ups
                                          driver.parameter.pollfreq: 30
                                          driver.parameter.pollinterval: 2
                                          driver.parameter.port: auto
                                          driver.version: 2.7.2
                                          driver.version.data: APC HID 0.95
                                          driver.version.internal: 0.38
                                          input.sensitivity: medium
                                          input.transfer.high: 147
                                          input.transfer.low: 88
                                          input.voltage: 126.0
                                          input.voltage.nominal: 120
                                          ups.beeper.status: disabled
                                          ups.delay.shutdown: 20
                                          ups.firmware: 868.L1 .D
                                          ups.firmware.aux: L1  
                                          ups.load: 3
                                          ups.mfr: American Power Conversion
                                          ups.mfr.date: 2010/12/15
                                          ups.model: Back-UPS BR1000G
                                          ups.productid: 0002
                                          ups.realpower.nominal: 600
                                          ups.serial: 3B1051X20349  
                                          ups.status: OL
                                          ups.test.result: No test initiated
                                          ups.timer.reboot: 0
                                          ups.timer.shutdown: -1
                                          ups.vendorid: 051d
                                          pi@bna-pwr-pi-01:~ $ 
                                          
                                          1 Reply Last reply Reply Quote 0
                                          • JaredBuschJ
                                            JaredBusch
                                            last edited by

                                            Unplugged the power and had some good news, some bad.

                                            The WALL commands spammed me, so I know things fired.

                                            The syslog though showed an error about permissions for PIPE/LOCK. See the message about failed to connect to parent.

                                            Feb  2 04:32:33 bna-pwr-pi-01 upsmon[737]: UPS bnajaredrouter@localhost on battery
                                            Feb  2 04:32:41 bna-pwr-pi-01 upssched[805]: Failed to connect to parent and failed to create parent: No such file or directory
                                            Feb  2 04:33:03 bna-pwr-pi-01 upsmon[737]: UPS bnajaredrouter@localhost on line power
                                            Feb  2 04:33:03 bna-pwr-pi-01 upssched[811]: Executing command: ongrid
                                            Feb  2 04:33:03 bna-pwr-pi-01 upssched-cmd: The UPS is now on grid power.
                                            

                                            Time to check the permissions.

                                            1 Reply Last reply Reply Quote 0