    Pi as a UPS monitor

    IT Discussion
    raspberry pi ups apc eaton nut
    8
    114
    33.8k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • JaredBuschJ
      JaredBusch @gjacobse
      last edited by

      @gjacobse said in Pi as a UPS monitor:

      @JaredBusch said in Pi as a UPS monitor:

      So ordering this one today.
      0_1475504077029_upload-aa8ddcff-9cac-498e-b4cb-3ea84837d1d0

      Why a 32GB card? Just because the cost is like - nothing?

      Because Amazon recommended it and I did not want to spend even 5 seconds finding my own card.

      Also This one will be used for a few more things than just the UPS monitor after I work out that process and figure our what device to buy multiples of.

      gjacobseG 1 Reply Last reply Reply Quote 2
      • gjacobseG
        gjacobse @JaredBusch
        last edited by

        @JaredBusch said in Pi as a UPS monitor:

        Why a 32GB card? Just because the cost is like - nothing?

        Because Amazon recommended it and I did not want to spend even 5 seconds finding my own card.

        Also This one will be used for a few more things than just the UPS monitor after I work out that process and figure our what device to buy multiples of.

        understandable.

        1 Reply Last reply Reply Quote 0
        • JaredBuschJ
          JaredBusch
          last edited by

          Now to see if I can get time to work on this before next week.

          https://instagram.ford1-1.fna.fbcdn.net/t51.2885-15/e35/14515863_1706849212971728_2069766214778880000_n.jpg

          gjacobseG 1 Reply Last reply Reply Quote 2
          • gjacobseG
            gjacobse @JaredBusch
            last edited by

            @JaredBusch said in Pi as a UPS monitor:

            Now to see if I can get time to work on this before next week.

            https://instagram.ford1-1.fna.fbcdn.net/t51.2885-15/e35/14515863_1706849212971728_2069766214778880000_n.jpg

            We are waiting with baited breath....

            travisdh1T 1 Reply Last reply Reply Quote 0
            • travisdh1T
              travisdh1 @gjacobse
              last edited by

              @gjacobse said in Pi as a UPS monitor:

              @JaredBusch said in Pi as a UPS monitor:

              Now to see if I can get time to work on this before next week.

              https://instagram.ford1-1.fna.fbcdn.net/t51.2885-15/e35/14515863_1706849212971728_2069766214778880000_n.jpg

              We are waiting with baited breath....

              I sense doubt, doubt leads to the dark side. Do or do not, @JaredBusch does not try.

              1 Reply Last reply Reply Quote 1
              • JaredBuschJ
                JaredBusch
                last edited by

                pi@raspberrypi:~ $ sudo upsc jaredoffice@localhost
                Init SSL without certificate database
                battery.charge: 100
                battery.charge.low: 10
                battery.charge.warning: 50
                battery.date: 2001/09/25
                battery.mfr.date: 2010/12/15
                battery.runtime: 1580
                battery.runtime.low: 120
                battery.type: PbAc
                battery.voltage: 27.2
                battery.voltage.nominal: 24.0
                device.mfr: American Power Conversion
                device.model: Back-UPS BR1000G
                device.serial: 3B1051X20329
                device.type: ups
                driver.name: usbhid-ups
                driver.parameter.pollfreq: 30
                driver.parameter.pollinterval: 2
                driver.parameter.port: auto
                driver.version: 2.7.2
                driver.version.data: APC HID 0.95
                driver.version.internal: 0.38
                input.sensitivity: medium
                input.transfer.high: 147
                input.transfer.low: 88
                input.voltage: 126.0
                input.voltage.nominal: 120
                ups.beeper.status: enabled
                ups.delay.shutdown: 20
                ups.firmware: 868.L1 .D
                ups.firmware.aux: L1
                ups.load: 18
                ups.mfr: American Power Conversion
                ups.mfr.date: 2010/12/15
                ups.model: Back-UPS BR1000G
                ups.productid: 0002
                ups.realpower.nominal: 600
                ups.serial: 3B1051X20329
                ups.status: OL
                ups.test.result: No test initiated
                ups.timer.reboot: 0
                ups.timer.shutdown: -1
                ups.vendorid: 051d
                pi@raspberrypi:~ $
                
                1 Reply Last reply Reply Quote 2
                • JaredBuschJ
                  JaredBusch
                  last edited by

                  Hopefully I can get it to do something tomorrow. no more time tonight.

                  1 Reply Last reply Reply Quote 0
                  • JaredBuschJ
                    JaredBusch
                    last edited by JaredBusch

                    Instructions assuming a Pi3

                    1. Install NOOBS to the SD Card.
                    2. Boot the Pi to NOOBS
                    3. Connect to wifi
                    4. Once it sees internet you can choose to install a minimal version of raspbian with no GUI
                    5. wait
                    6. login with default creds pi/raspberry
                    7. run sudo raspi-config to enable SSH and optionally set other options you want.
                    8. edit the wifi config file sudo nano /etc/wpa_supplicant/wpa_supplicant.conf
                      network={
                      ssid="yourssid"
                      psk="ssidpassword"
                      }
                    9. reboot the Pi3
                    10. update raspian
                      1. sudo apt-get update
                      2. sudo apt-get upgrade
                    11. Install nut
                      1. sudo apt-get install nut
                    12. Edit sudo nano /etc/nut/nut.conf
                      1. change MODE=standalone
                    13. Edit sudo nano /etc/nut/ups.conf
                    14. add a block at the end of the file.
                      1. a default example
                        [somenameforups]
                        driver = usbhid-ups
                        port = auto
                        desc = "Some descriptive name for UPS"
                      2. what mine is
                        [jaredoffice]
                        driver = usbhid-ups
                        port = auto
                        desc = "Jared's Desk"
                    15. Test the conf file is right sudo upsdrvctl start
                    16. Launch the UPS daemon sudo upsd
                    17. see if it is talking sudo upsc somenameforups@localhost
                      1. or my real one sudo upsc jaredoffice@localhost
                    1 Reply Last reply Reply Quote 3
                    • gjacobseG
                      gjacobse
                      last edited by

                      Interesting that the last two of the last three messages seem out of order. But - great information.

                      1 Reply Last reply Reply Quote 0
                      • gjacobseG
                        gjacobse
                        last edited by gjacobse

                        Well - while I don't have a Pi yet, I do happen to have a LM 17.x system running as my Pandora Music box (Pithos). It's within reach of one of the several UPS units I have (I have like nine) so I used your process and got one set up:

                        sudo upsc pandora
                        :
                        Init SSL without certificate database
                        battery.charge: 100
                        battery.charge.low: 10
                        battery.charge.warning: 50
                        battery.date: not set
                        battery.mfr.date: 2014/06/22
                        battery.runtime: 3336
                        battery.runtime.low: 120
                        battery.type: PbAc
                        battery.voltage: 13.5
                        battery.voltage.nominal: 12.0
                        device.mfr: APC
                        device.model: Back-UPS ES 550G
                        device.serial: 4B1425P54201
                        device.type: ups
                        driver.name: usbhid-ups
                        driver.parameter.pollfreq: 30
                        driver.parameter.pollinterval: 2
                        driver.parameter.port: auto
                        driver.version: 2.7.1
                        driver.version.data: APC HID 0.95
                        driver.version.internal: 0.38
                        input.sensitivity: medium
                        input.transfer.high: 139
                        input.transfer.low: 92
                        input.voltage: 125.0
                        input.voltage.nominal: 120
                        ups.beeper.status: enabled
                        ups.delay.shutdown: 20
                        ups.firmware: 904.W1 .D
                        ups.firmware.aux: W1
                        ups.load: 12
                        ups.mfr: APC
                        ups.mfr.date: 2014/06/22
                        ups.model: Back-UPS ES 550G
                        ups.productid: 0002
                        ups.serial: 4B1425P54201
                        ups.status: OL
                        ups.timer.reboot: 0
                        ups.timer.shutdown: -1
                        ups.vendorid: 051d
                        
                        1 Reply Last reply Reply Quote 1
                        • JaredBuschJ
                          JaredBusch
                          last edited by

                          Today will be tinkering with notification options.

                          1 Reply Last reply Reply Quote 2
                          • gjacobseG
                            gjacobse
                            last edited by

                            Just got this:

                            Init SSL without certificate database
                            Error: Data stale
                            
                            1 Reply Last reply Reply Quote 0
                            • gjacobseG
                              gjacobse
                              last edited by

                              Went back through the commands above to validation / confirmation:

                              $ sudo nano /etc/nut/nut.conf
                              

                              no changes - the same.

                              $ sudo nano /etc/nut/ups.conf
                              

                              no changes - the same

                               $ sudo upsdrvctl start
                              Network UPS Tools - UPS driver controller 2.7.1
                              Network UPS Tools - Generic HID driver 0.38 (2.7.1)
                              USB communication driver 0.32
                              Duplicate driver instance detected! Terminating other driver!
                              Using subdriver: APC HID 0.95
                              

                              Okay - seems 'ok'

                              $ sudo upsd
                              Network UPS Tools upsd 2.7.1
                              fopen /var/run/nut/upsd.pid: No such file or directory
                              not listening on 127.0.0.1 port 3493
                              not listening on ::1 port 3493
                              no listening interface available
                              
                              $ sudo upsc pandora
                              Init SSL without certificate database
                              Error: Data stale
                              

                              curious.

                              JaredBuschJ 1 Reply Last reply Reply Quote 0
                              • JaredBuschJ
                                JaredBusch @gjacobse
                                last edited by

                                @gjacobse I do not get that. Mine has been untouched since last night.

                                pi@raspberrypi:~ $ sudo upsc jaredoffice
                                Init SSL without certificate database
                                battery.charge: 100
                                battery.charge.low: 10
                                battery.charge.warning: 50
                                battery.date: 2001/09/25
                                battery.mfr.date: 2010/12/15
                                battery.runtime: 1472
                                battery.runtime.low: 120
                                battery.type: PbAc
                                battery.voltage: 27.2
                                battery.voltage.nominal: 24.0
                                device.mfr: American Power Conversion
                                device.model: Back-UPS BR1000G
                                device.serial: 3B1051X20329
                                device.type: ups
                                driver.name: usbhid-ups
                                driver.parameter.pollfreq: 30
                                driver.parameter.pollinterval: 2
                                driver.parameter.port: auto
                                driver.version: 2.7.2
                                driver.version.data: APC HID 0.95
                                driver.version.internal: 0.38
                                input.sensitivity: medium
                                input.transfer.high: 147
                                input.transfer.low: 88
                                input.voltage: 124.0
                                input.voltage.nominal: 120
                                ups.beeper.status: enabled
                                ups.delay.shutdown: 20
                                ups.firmware: 868.L1 .D
                                ups.firmware.aux: L1
                                ups.load: 20
                                ups.mfr: American Power Conversion
                                ups.mfr.date: 2010/12/15
                                ups.model: Back-UPS BR1000G
                                ups.productid: 0002
                                ups.realpower.nominal: 600
                                ups.serial: 3B1051X20329
                                ups.status: OL
                                ups.test.result: No test initiated
                                ups.timer.reboot: 0
                                ups.timer.shutdown: -1
                                ups.vendorid: 051d
                                pi@raspberrypi:~ $
                                
                                1 Reply Last reply Reply Quote 0
                                • JaredBuschJ
                                  JaredBusch
                                  last edited by

                                  This is what I will be following to configure reporting/alerting.
                                  http://www.techrepublic.com/article/customize-ups-related-alerts-in-nut/

                                  gjacobseG 1 Reply Last reply Reply Quote 1
                                  • gjacobseG
                                    gjacobse @JaredBusch
                                    last edited by

                                    @JaredBusch
                                    Well push comes to Meh -okay. I restarted the box and it's polls now.

                                    Won't do anything else with it for a spell to see if it retains it. It's been four days since I restarted it. Now - to reconnect to it as I had to pull the monitor off. X2Go works great,.. but only once I've signed in at the local. sure that is omething that can be changed.

                                    1 Reply Last reply Reply Quote 0
                                    • gjacobseG
                                      gjacobse
                                      last edited by

                                      checking on my UPS this morning

                                       ~ $ uptime
                                       09:59:20 up 6 days, 18:12,  2 users,  load average: 0.19, 0.25, 0.25
                                      
                                       ~ $ sudo upsc pandora
                                      Init SSL without certificate database
                                      battery.charge: 100
                                      battery.charge.low: 10
                                      battery.charge.warning: 50
                                      battery.date: not set
                                      battery.mfr.date: 2014/06/22
                                      battery.runtime: 3172
                                      battery.runtime.low: 120
                                      battery.type: PbAc
                                      battery.voltage: 13.6
                                      battery.voltage.nominal: 12.0
                                      device.mfr: APC
                                      device.model: Back-UPS ES 550G
                                      device.serial: 4B1425P54201
                                      device.type: ups
                                      driver.name: usbhid-ups
                                      driver.parameter.pollfreq: 30
                                      driver.parameter.pollinterval: 2
                                      driver.parameter.port: auto
                                      driver.version: 2.7.1
                                      driver.version.data: APC HID 0.95
                                      driver.version.internal: 0.38
                                      input.sensitivity: medium
                                      input.transfer.high: 139
                                      input.transfer.low: 92
                                      input.voltage: 126.0
                                      input.voltage.nominal: 120
                                      ups.beeper.status: enabled
                                      ups.delay.shutdown: 20
                                      ups.firmware: 904.W1 .D
                                      ups.firmware.aux: W1
                                      ups.load: 13
                                      ups.mfr: APC
                                      ups.mfr.date: 2014/06/22
                                      ups.model: Back-UPS ES 550G
                                      ups.productid: 0002
                                      ups.serial: 4B1425P54201
                                      ups.status: OL
                                      ups.timer.reboot: 0
                                      ups.timer.shutdown: -1
                                      ups.vendorid: 051d
                                      

                                      Since reboot, the monitor has been running all the time. So it may have been simply that.

                                      As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

                                      gjacobseG travisdh1T thwrT 3 Replies Last reply Reply Quote 1
                                      • gjacobseG
                                        gjacobse @gjacobse
                                        last edited by

                                        @gjacobse said in Pi as a UPS monitor:

                                        checking on my UPS this morning

                                        Since reboot, the monitor has been running all the time. So it may have been simply that.

                                        As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

                                        Maybe something similar to the UBNT controller software - central configuration ability.....

                                        1 Reply Last reply Reply Quote 0
                                        • travisdh1T
                                          travisdh1 @gjacobse
                                          last edited by

                                          @gjacobse said in Pi as a UPS monitor:

                                          checking on my UPS this morning

                                           ~ $ uptime
                                           09:59:20 up 6 days, 18:12,  2 users,  load average: 0.19, 0.25, 0.25
                                          
                                           ~ $ sudo upsc pandora
                                          Init SSL without certificate database
                                          battery.charge: 100
                                          battery.charge.low: 10
                                          battery.charge.warning: 50
                                          battery.date: not set
                                          battery.mfr.date: 2014/06/22
                                          battery.runtime: 3172
                                          battery.runtime.low: 120
                                          battery.type: PbAc
                                          battery.voltage: 13.6
                                          battery.voltage.nominal: 12.0
                                          device.mfr: APC
                                          device.model: Back-UPS ES 550G
                                          device.serial: 4B1425P54201
                                          device.type: ups
                                          driver.name: usbhid-ups
                                          driver.parameter.pollfreq: 30
                                          driver.parameter.pollinterval: 2
                                          driver.parameter.port: auto
                                          driver.version: 2.7.1
                                          driver.version.data: APC HID 0.95
                                          driver.version.internal: 0.38
                                          input.sensitivity: medium
                                          input.transfer.high: 139
                                          input.transfer.low: 92
                                          input.voltage: 126.0
                                          input.voltage.nominal: 120
                                          ups.beeper.status: enabled
                                          ups.delay.shutdown: 20
                                          ups.firmware: 904.W1 .D
                                          ups.firmware.aux: W1
                                          ups.load: 13
                                          ups.mfr: APC
                                          ups.mfr.date: 2014/06/22
                                          ups.model: Back-UPS ES 550G
                                          ups.productid: 0002
                                          ups.serial: 4B1425P54201
                                          ups.status: OL
                                          ups.timer.reboot: 0
                                          ups.timer.shutdown: -1
                                          ups.vendorid: 051d
                                          

                                          Since reboot, the monitor has been running all the time. So it may have been simply that.

                                          As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

                                          Take the output of upsc and throw it up on a web page. Unless you want a local display, in which case it's actually more difficult.

                                          1 Reply Last reply Reply Quote 0
                                          • thwrT
                                            thwr @gjacobse
                                            last edited by

                                            @gjacobse said in Pi as a UPS monitor:

                                            checking on my UPS this morning

                                             ~ $ uptime
                                             09:59:20 up 6 days, 18:12,  2 users,  load average: 0.19, 0.25, 0.25
                                            
                                             ~ $ sudo upsc pandora
                                            Init SSL without certificate database
                                            battery.charge: 100
                                            battery.charge.low: 10
                                            battery.charge.warning: 50
                                            battery.date: not set
                                            battery.mfr.date: 2014/06/22
                                            battery.runtime: 3172
                                            battery.runtime.low: 120
                                            battery.type: PbAc
                                            battery.voltage: 13.6
                                            battery.voltage.nominal: 12.0
                                            device.mfr: APC
                                            device.model: Back-UPS ES 550G
                                            device.serial: 4B1425P54201
                                            device.type: ups
                                            driver.name: usbhid-ups
                                            driver.parameter.pollfreq: 30
                                            driver.parameter.pollinterval: 2
                                            driver.parameter.port: auto
                                            driver.version: 2.7.1
                                            driver.version.data: APC HID 0.95
                                            driver.version.internal: 0.38
                                            input.sensitivity: medium
                                            input.transfer.high: 139
                                            input.transfer.low: 92
                                            input.voltage: 126.0
                                            input.voltage.nominal: 120
                                            ups.beeper.status: enabled
                                            ups.delay.shutdown: 20
                                            ups.firmware: 904.W1 .D
                                            ups.firmware.aux: W1
                                            ups.load: 13
                                            ups.mfr: APC
                                            ups.mfr.date: 2014/06/22
                                            ups.model: Back-UPS ES 550G
                                            ups.productid: 0002
                                            ups.serial: 4B1425P54201
                                            ups.status: OL
                                            ups.timer.reboot: 0
                                            ups.timer.shutdown: -1
                                            ups.vendorid: 051d
                                            

                                            Since reboot, the monitor has been running all the time. So it may have been simply that.

                                            As for having multiple UPS monitoring, I was curious what you thought about having a central display which showed the status of each UPS monitored. That way you have one display to glance at for a health check.

                                            AMQP / MQTT may be awesome for this at the transport layer. MQTT is an interesting protocol that let you define a "last will and testament" action in case something goes south.

                                            Ansible/Puppet etc. can handle the central configuration.

                                            1 Reply Last reply Reply Quote 1