      So ordering this one today.
      0_1475504077029_upload-aa8ddcff-9cac-498e-b4cb-3ea84837d1d0

      IRJI gjacobseG 2 Replies Last reply Reply Quote 2
      • IRJI
        IRJ @JaredBusch
        last edited by

        @JaredBusch said in Pi as a UPS monitor:

        So ordering this one today.
        0_1475504077029_upload-aa8ddcff-9cac-498e-b4cb-3ea84837d1d0

        I used the same kit and same micro SD card lol

        JaredBuschJ 1 Reply Last reply Reply Quote 0
        • JaredBuschJ
          JaredBusch @IRJ
          last edited by JaredBusch

          @IRJ said in Pi as a UPS monitor:

          I used the same kit and same micro SD card lol

          Any specific project?

          IRJI 1 Reply Last reply Reply Quote 0
          • IRJI
            IRJ @JaredBusch
            last edited by

            @JaredBusch said in Pi as a UPS monitor:

            @IRJ said in Pi as a UPS monitor:

            I used the same kit and same micro SD card lol

            Any specific project?

            I am just running OpenElec on that particular unit.

            1 Reply Last reply Reply Quote 0
            • gjacobseG
              gjacobse @JaredBusch
              last edited by

              @JaredBusch said in Pi as a UPS monitor:

              So ordering this one today.
              0_1475504077029_upload-aa8ddcff-9cac-498e-b4cb-3ea84837d1d0

              Why a 32GB card? Just because the cost is like - nothing?

              JaredBuschJ 1 Reply Last reply Reply Quote 0
              • JaredBuschJ
                JaredBusch @gjacobse
                last edited by

                @gjacobse said in Pi as a UPS monitor:

                @JaredBusch said in Pi as a UPS monitor:

                So ordering this one today.
                0_1475504077029_upload-aa8ddcff-9cac-498e-b4cb-3ea84837d1d0

                Why a 32GB card? Just because the cost is like - nothing?

                Because Amazon recommended it and I did not want to spend even 5 seconds finding my own card.

                Also This one will be used for a few more things than just the UPS monitor after I work out that process and figure our what device to buy multiples of.

                gjacobseG 1 Reply Last reply Reply Quote 2
                • gjacobseG
                  gjacobse @JaredBusch
                  last edited by

                  @JaredBusch said in Pi as a UPS monitor:

                  Why a 32GB card? Just because the cost is like - nothing?

                  Because Amazon recommended it and I did not want to spend even 5 seconds finding my own card.

                  Also This one will be used for a few more things than just the UPS monitor after I work out that process and figure our what device to buy multiples of.

                  understandable.

                  1 Reply Last reply Reply Quote 0
                  • JaredBuschJ
                    JaredBusch
                    last edited by

                    Now to see if I can get time to work on this before next week.

                    https://instagram.ford1-1.fna.fbcdn.net/t51.2885-15/e35/14515863_1706849212971728_2069766214778880000_n.jpg

                    gjacobseG 1 Reply Last reply Reply Quote 2
                    • gjacobseG
                      gjacobse @JaredBusch
                      last edited by

                      @JaredBusch said in Pi as a UPS monitor:

                      Now to see if I can get time to work on this before next week.

                      https://instagram.ford1-1.fna.fbcdn.net/t51.2885-15/e35/14515863_1706849212971728_2069766214778880000_n.jpg

                      We are waiting with baited breath....

                      travisdh1T 1 Reply Last reply Reply Quote 0
                      • travisdh1T
                        travisdh1 @gjacobse
                        last edited by

                        @gjacobse said in Pi as a UPS monitor:

                        @JaredBusch said in Pi as a UPS monitor:

                        Now to see if I can get time to work on this before next week.

                        https://instagram.ford1-1.fna.fbcdn.net/t51.2885-15/e35/14515863_1706849212971728_2069766214778880000_n.jpg

                        We are waiting with baited breath....

                        I sense doubt, doubt leads to the dark side. Do or do not, @JaredBusch does not try.

                        1 Reply Last reply Reply Quote 1
                        • JaredBuschJ
                          JaredBusch
                          last edited by

                          pi@raspberrypi:~ $ sudo upsc jaredoffice@localhost
                          Init SSL without certificate database
                          battery.charge: 100
                          battery.charge.low: 10
                          battery.charge.warning: 50
                          battery.date: 2001/09/25
                          battery.mfr.date: 2010/12/15
                          battery.runtime: 1580
                          battery.runtime.low: 120
                          battery.type: PbAc
                          battery.voltage: 27.2
                          battery.voltage.nominal: 24.0
                          device.mfr: American Power Conversion
                          device.model: Back-UPS BR1000G
                          device.serial: 3B1051X20329
                          device.type: ups
                          driver.name: usbhid-ups
                          driver.parameter.pollfreq: 30
                          driver.parameter.pollinterval: 2
                          driver.parameter.port: auto
                          driver.version: 2.7.2
                          driver.version.data: APC HID 0.95
                          driver.version.internal: 0.38
                          input.sensitivity: medium
                          input.transfer.high: 147
                          input.transfer.low: 88
                          input.voltage: 126.0
                          input.voltage.nominal: 120
                          ups.beeper.status: enabled
                          ups.delay.shutdown: 20
                          ups.firmware: 868.L1 .D
                          ups.firmware.aux: L1
                          ups.load: 18
                          ups.mfr: American Power Conversion
                          ups.mfr.date: 2010/12/15
                          ups.model: Back-UPS BR1000G
                          ups.productid: 0002
                          ups.realpower.nominal: 600
                          ups.serial: 3B1051X20329
                          ups.status: OL
                          ups.test.result: No test initiated
                          ups.timer.reboot: 0
                          ups.timer.shutdown: -1
                          ups.vendorid: 051d
                          pi@raspberrypi:~ $
                          
                          1 Reply Last reply Reply Quote 2
                          • JaredBuschJ
                            JaredBusch
                            last edited by

                            Hopefully I can get it to do something tomorrow. no more time tonight.

                            1 Reply Last reply Reply Quote 0
                            • JaredBuschJ
                              JaredBusch
                              last edited by JaredBusch

                              Instructions assuming a Pi3

                              1. Install NOOBS to the SD Card.
                              2. Boot the Pi to NOOBS
                              3. Connect to wifi
                              4. Once it sees internet you can choose to install a minimal version of raspbian with no GUI
                              5. wait
                              6. login with default creds pi/raspberry
                              7. run sudo raspi-config to enable SSH and optionally set other options you want.
                              8. edit the wifi config file sudo nano /etc/wpa_supplicant/wpa_supplicant.conf
                                network={
                                ssid="yourssid"
                                psk="ssidpassword"
                                }
                              9. reboot the Pi3
                              10. update raspian
                                1. sudo apt-get update
                                2. sudo apt-get upgrade
                              11. Install nut
                                1. sudo apt-get install nut
                              12. Edit sudo nano /etc/nut/nut.conf
                                1. change MODE=standalone
                              13. Edit sudo nano /etc/nut/ups.conf
                              14. add a block at the end of the file.
                                1. a default example
                                  [somenameforups]
                                  driver = usbhid-ups
                                  port = auto
                                  desc = "Some descriptive name for UPS"
                                2. what mine is
                                  [jaredoffice]
                                  driver = usbhid-ups
                                  port = auto
                                  desc = "Jared's Desk"
                              15. Test the conf file is right sudo upsdrvctl start
                              16. Launch the UPS daemon sudo upsd
                              17. see if it is talking sudo upsc somenameforups@localhost
                                1. or my real one sudo upsc jaredoffice@localhost
                              1 Reply Last reply Reply Quote 3
                              • gjacobseG
                                gjacobse
                                last edited by

                                Interesting that the last two of the last three messages seem out of order. But - great information.

                                1 Reply Last reply Reply Quote 0
                                • gjacobseG
                                  gjacobse
                                  last edited by gjacobse

                                  Well - while I don't have a Pi yet, I do happen to have a LM 17.x system running as my Pandora Music box (Pithos). It's within reach of one of the several UPS units I have (I have like nine) so I used your process and got one set up:

                                  sudo upsc pandora
                                  :
                                  Init SSL without certificate database
                                  battery.charge: 100
                                  battery.charge.low: 10
                                  battery.charge.warning: 50
                                  battery.date: not set
                                  battery.mfr.date: 2014/06/22
                                  battery.runtime: 3336
                                  battery.runtime.low: 120
                                  battery.type: PbAc
                                  battery.voltage: 13.5
                                  battery.voltage.nominal: 12.0
                                  device.mfr: APC
                                  device.model: Back-UPS ES 550G
                                  device.serial: 4B1425P54201
                                  device.type: ups
                                  driver.name: usbhid-ups
                                  driver.parameter.pollfreq: 30
                                  driver.parameter.pollinterval: 2
                                  driver.parameter.port: auto
                                  driver.version: 2.7.1
                                  driver.version.data: APC HID 0.95
                                  driver.version.internal: 0.38
                                  input.sensitivity: medium
                                  input.transfer.high: 139
                                  input.transfer.low: 92
                                  input.voltage: 125.0
                                  input.voltage.nominal: 120
                                  ups.beeper.status: enabled
                                  ups.delay.shutdown: 20
                                  ups.firmware: 904.W1 .D
                                  ups.firmware.aux: W1
                                  ups.load: 12
                                  ups.mfr: APC
                                  ups.mfr.date: 2014/06/22
                                  ups.model: Back-UPS ES 550G
                                  ups.productid: 0002
                                  ups.serial: 4B1425P54201
                                  ups.status: OL
                                  ups.timer.reboot: 0
                                  ups.timer.shutdown: -1
                                  ups.vendorid: 051d
                                  
                                  1 Reply Last reply Reply Quote 1
                                  • JaredBuschJ
                                    JaredBusch
                                    last edited by

                                    Today will be tinkering with notification options.

                                    1 Reply Last reply Reply Quote 2
                                    • gjacobseG
                                      gjacobse
                                      last edited by

                                      Just got this:

                                      Init SSL without certificate database
                                      Error: Data stale
                                      
                                      1 Reply Last reply Reply Quote 0
                                      • gjacobseG
                                        gjacobse
                                        last edited by

                                        Went back through the commands above to validation / confirmation:

                                        $ sudo nano /etc/nut/nut.conf
                                        

                                        no changes - the same.

                                        $ sudo nano /etc/nut/ups.conf
                                        

                                        no changes - the same

                                         $ sudo upsdrvctl start
                                        Network UPS Tools - UPS driver controller 2.7.1
                                        Network UPS Tools - Generic HID driver 0.38 (2.7.1)
                                        USB communication driver 0.32
                                        Duplicate driver instance detected! Terminating other driver!
                                        Using subdriver: APC HID 0.95
                                        

                                        Okay - seems 'ok'

                                        $ sudo upsd
                                        Network UPS Tools upsd 2.7.1
                                        fopen /var/run/nut/upsd.pid: No such file or directory
                                        not listening on 127.0.0.1 port 3493
                                        not listening on ::1 port 3493
                                        no listening interface available
                                        
                                        $ sudo upsc pandora
                                        Init SSL without certificate database
                                        Error: Data stale
                                        

                                        curious.

                                        JaredBuschJ 1 Reply Last reply Reply Quote 0
                                        • JaredBuschJ
                                          JaredBusch @gjacobse
                                          last edited by

                                          @gjacobse I do not get that. Mine has been untouched since last night.

                                          pi@raspberrypi:~ $ sudo upsc jaredoffice
                                          Init SSL without certificate database
                                          battery.charge: 100
                                          battery.charge.low: 10
                                          battery.charge.warning: 50
                                          battery.date: 2001/09/25
                                          battery.mfr.date: 2010/12/15
                                          battery.runtime: 1472
                                          battery.runtime.low: 120
                                          battery.type: PbAc
                                          battery.voltage: 27.2
                                          battery.voltage.nominal: 24.0
                                          device.mfr: American Power Conversion
                                          device.model: Back-UPS BR1000G
                                          device.serial: 3B1051X20329
                                          device.type: ups
                                          driver.name: usbhid-ups
                                          driver.parameter.pollfreq: 30
                                          driver.parameter.pollinterval: 2
                                          driver.parameter.port: auto
                                          driver.version: 2.7.2
                                          driver.version.data: APC HID 0.95
                                          driver.version.internal: 0.38
                                          input.sensitivity: medium
                                          input.transfer.high: 147
                                          input.transfer.low: 88
                                          input.voltage: 124.0
                                          input.voltage.nominal: 120
                                          ups.beeper.status: enabled
                                          ups.delay.shutdown: 20
                                          ups.firmware: 868.L1 .D
                                          ups.firmware.aux: L1
                                          ups.load: 20
                                          ups.mfr: American Power Conversion
                                          ups.mfr.date: 2010/12/15
                                          ups.model: Back-UPS BR1000G
                                          ups.productid: 0002
                                          ups.realpower.nominal: 600
                                          ups.serial: 3B1051X20329
                                          ups.status: OL
                                          ups.test.result: No test initiated
                                          ups.timer.reboot: 0
                                          ups.timer.shutdown: -1
                                          ups.vendorid: 051d
                                          pi@raspberrypi:~ $
                                          
                                          1 Reply Last reply Reply Quote 0
                                          • JaredBuschJ
                                            JaredBusch
                                            last edited by

                                            This is what I will be following to configure reporting/alerting.
                                            http://www.techrepublic.com/article/customize-ups-related-alerts-in-nut/

                                            gjacobseG 1 Reply Last reply Reply Quote 1