      In this case, I would suggest doing some performance tests on your existing ERP server to see how many iops you have currently, then see what you will get with various disks in RAID10

      1 Reply Last reply Reply Quote 1
      • wrx7mW
        wrx7m
        last edited by

        I didn't realize enterprise SSDs had come down enough to compete with 15k drives. Interesting.

        KellyK scottalanmillerS 2 Replies Last reply Reply Quote 0
        • KellyK
          Kelly @wrx7m
          last edited by Kelly

          @wrx7m said in RAID recommendation for Hyper-V host:

          I didn't realize enterprise SSDs had come down enough to compete with 15k drives. Interesting.

          https://www.neweggbusiness.com/product/product.aspx?item=9b-2rc-0034-000b7 = $0.53 per GB. It is still more, but the value can be justified, imo.

          1 Reply Last reply Reply Quote 1
          • DashrenderD
            Dashrender
            last edited by

            If going with Dell, Xbyte has

            https://i.imgur.com/RkmYKlF.png

            So you'd need 4 in RAID 10 to get enough storage for your situation. 960 GB is the largest drives I see on Xbyte when sorting by the R730.

            1 Reply Last reply Reply Quote 0
            • scottalanmillerS
              scottalanmiller @i3
              last edited by

              @i3 said in RAID recommendation for Hyper-V host:

              Our ERP data size is around 400GB and our file server data size is around 700GB.

              ...

              Should I add more drives to the second array or create a third array with less expensive drives since our file server doesn't require 15k drives.

              Couple approaches here that tend to make sense. Here are the two that I would consider most strongly:

              1. Single array. Use 10K drives and a lot of them. Six 10K drives is the same speed as four 15K drives. So use eight or more here, get more speed for everything. The OS, the data, the DB all on a single array. More speed for everything.

              2. Split array. Use NS-SAS or 7200 RPM SATA drives for the OS and the file server data. Use RAID 1 SSDs for the database.

              1 Reply Last reply Reply Quote 1
              • scottalanmillerS
                scottalanmiller @wrx7m
                last edited by

                @wrx7m said in RAID recommendation for Hyper-V host:

                I didn't realize enterprise SSDs had come down enough to compete with 15k drives. Interesting.

                Have for a while. The trick is compare by IOPS rather than by capacity.

                DashrenderD 1 Reply Last reply Reply Quote 1
                • DashrenderD
                  Dashrender @scottalanmiller
                  last edited by

                  @scottalanmiller said in RAID recommendation for Hyper-V host:

                  @wrx7m said in RAID recommendation for Hyper-V host:

                  I didn't realize enterprise SSDs had come down enough to compete with 15k drives. Interesting.

                  Have for a while. The trick is compare by IOPS rather than by capacity.

                  But it's exactly that, a trick. It's all about making numbers do whatever you want them to do.

                  scottalanmillerS 1 Reply Last reply Reply Quote 0
                  • DashrenderD
                    Dashrender
                    last edited by

                    Xbyte had 15K drives at
                    https://i.imgur.com/44OL5yh.png

                    So at the high end, assuming 6 drives, you're looking at $2094 vs $4196 for SSD

                    Of course, the SSD is going to swim circles around those other drives performance wise.

                    1 Reply Last reply Reply Quote 0
                    • DashrenderD
                      Dashrender @i3
                      last edited by

                      @i3 said in RAID recommendation for Hyper-V host:

                      We are looking to purchase a Hyper-V host to consolidate a few of our physical servers. The two main servers would be our file server and an ERP system. The ERP system is supported on Hyper-V, however their recommended RAID is as follows:
                      Two drive Raid 1 for the OS
                      min. 4 drive Raid 1+0 for the data array (15k SAS)

                      Our ERP data size is around 400GB and our file server data size is around 700GB.

                      My thoughts were to put the virtual machines OS' on the two drive raid 1 array and the data drives for both our ERP and file server on the second array. At are current data usage, (4) 600GB 15k SAS drives would not be leaving us much more room for growth.
                      Should I add more drives to the second array or create a third array with less expensive drives since our file server doesn't require 15k drives.

                      Thanks,
                      G

                      Do you know your IOPs usage? What is the drive array configuration of your ERP currently? We can do some real rough calculations based on that (type of drive, RPM, number of drives in each array, etc).

                      1 Reply Last reply Reply Quote 0
                      • scottalanmillerS
                        scottalanmiller @Dashrender
                        last edited by

                        @Dashrender said in RAID recommendation for Hyper-V host:

                        @scottalanmiller said in RAID recommendation for Hyper-V host:

                        @wrx7m said in RAID recommendation for Hyper-V host:

                        I didn't realize enterprise SSDs had come down enough to compete with 15k drives. Interesting.

                        Have for a while. The trick is compare by IOPS rather than by capacity.

                        But it's exactly that, a trick. It's all about making numbers do whatever you want them to do.

                        It's not a trick at all in that sense. No more than using capacity as the sole gauge of storage value is a trick. It's like cars, sometimes you are shopping for speed, sometimes for capacity. If we only shopped for speed we'd only buy F1 cars. If we only shopped for capacity we'd only buy minivans. Everyone with something that isn't one of those two blended their needs.

                        DashrenderD 1 Reply Last reply Reply Quote 0
                        • wrx7mW
                          wrx7m
                          last edited by

                          He still needs to find out what his IOPS usage is, currently. Then make an educated guess what it will be in the next few years and decide which drives/configuration will support those results.

                          DashrenderD 1 Reply Last reply Reply Quote 0
                          • DashrenderD
                            Dashrender @scottalanmiller
                            last edited by

                            @scottalanmiller said in RAID recommendation for Hyper-V host:

                            @Dashrender said in RAID recommendation for Hyper-V host:

                            @scottalanmiller said in RAID recommendation for Hyper-V host:

                            @wrx7m said in RAID recommendation for Hyper-V host:

                            I didn't realize enterprise SSDs had come down enough to compete with 15k drives. Interesting.

                            Have for a while. The trick is compare by IOPS rather than by capacity.

                            But it's exactly that, a trick. It's all about making numbers do whatever you want them to do.

                            It's not a trick at all in that sense. No more than using capacity as the sole gauge of storage value is a trick. It's like cars, sometimes you are shopping for speed, sometimes for capacity. If we only shopped for speed we'd only buy F1 cars. If we only shopped for capacity we'd only buy minivans. Everyone with something that isn't one of those two blended their needs.

                            Well then don't say 'the trick is.' Instead say - put the cost in terms of the required context. If speed is context, then frame it that way, if capacity is the context, frame it that way.

                            1 Reply Last reply Reply Quote 0
                            • DashrenderD
                              Dashrender @wrx7m
                              last edited by

                              @wrx7m said in RAID recommendation for Hyper-V host:

                              He still needs to find out what his IOPS usage is, currently. Then make an educated guess what it will be in the next few years and decide which drives/configuration will support those results.

                              that's assuming his current load is not the bottleneck 😉

                              wrx7mW 1 Reply Last reply Reply Quote 0
                              • wrx7mW
                                wrx7m @Dashrender
                                last edited by wrx7m

                                @Dashrender He could find out if it were. Simply measure the IOPS and calculate the max IOPS of existing configuration. If they are close, then his current config is a bottleneck.

                                1 Reply Last reply Reply Quote 0
                                • JaredBuschJ
                                  JaredBusch
                                  last edited by

                                  @Dashrender said in RAID recommendation for Hyper-V host:

                                  If going with Dell, Xbyte has

                                  https://i.imgur.com/RkmYKlF.png

                                  So you'd need 4 in RAID 10 to get enough storage for your situation. 960 GB is the largest drives I see on Xbyte when sorting by the R730.

                                  WTF, SSD in RAID 10? Hello, reality to @Dashrender

                                  He needs 1.1 TB in array space give or take. So he could go with 4 400GB drives in RAID 5 for it all for half the price of 4 of the 960GB drives.

                                  0_1476244952165_upload-ee46ded2-6230-45e9-980c-1533be3d32ee

                                  Or more realistically, he can go with NL-SAS in RAID 10 for everything except the ERP database. Put the ERP on 2 400GB in RAID 1 or 3 in RAID 5.

                                  1 Reply Last reply Reply Quote 1
                                  • DashrenderD
                                    Dashrender
                                    last edited by

                                    Duh, you're right, my bad.

                                    Though the OP did voice concern about not having any left over storage... So your second solution would solve that.

                                    1 Reply Last reply Reply Quote 0
                                    • I
                                      i3
                                      last edited by

                                      Thank you for all the input. I will try to answer as many as the questions as I can.

                                      @wrx7m said in RAID recommendation for Hyper-V host:

                                      What server are you going to use as your host?

                                      Server 2012r2

                                      @scottalanmiller said in RAID recommendation for Hyper-V host:

                                      @i3 said in RAID recommendation for Hyper-V host:

                                      My thoughts were to put the virtual machines OS' on the two drive raid 1 array and the data drives for both our ERP and file server on the second array.

                                      Yup, that's fine. It would be better to have all six drives in a single array not in split arrays, but the split arrays aren't dangerous here, just not as good speed or capacity as merging them all into a single array. A single array would be better all around, no downsides.

                                      What type of RAID would be best in this scenario?

                                      @Dashrender said in RAID recommendation for Hyper-V host:

                                      @i3 said in RAID recommendation for Hyper-V host:

                                      We are looking to purchase a Hyper-V host to consolidate a few of our physical servers. The two main servers would be our file server and an ERP system. The ERP system is supported on Hyper-V, however their recommended RAID is as follows:
                                      Two drive Raid 1 for the OS
                                      min. 4 drive Raid 1+0 for the data array (15k SAS)

                                      Our ERP data size is around 400GB and our file server data size is around 700GB.

                                      My thoughts were to put the virtual machines OS' on the two drive raid 1 array and the data drives for both our ERP and file server on the second array. At are current data usage, (4) 600GB 15k SAS drives would not be leaving us much more room for growth.
                                      Should I add more drives to the second array or create a third array with less expensive drives since our file server doesn't require 15k drives.

                                      Thanks,
                                      G

                                      Do you know your IOPs usage? What is the drive array configuration of your ERP currently? We can do some real rough calculations based on that (type of drive, RPM, number of drives in each array, etc).

                                      I do not have a current IOP usage. The current config is a standalone server with two split arrays. OS is on a RAID 1 with two 15k drives; Data is on a RAID 1+0 with 4 15k drives. The only data I have currently is below. I know it may not be the best indicator but it is all I have at this point without collecting more data.
                                      Read Queue length: Spikes to 2/3 during peak usage hours otherwise at 0
                                      Write queue length: Spikes to just under 1 during peak usage hours (same as read) otherwise at 0
                                      Disk Busy Time%: Spikes between 80-100% during peak hours (same as above) otherwise at 0
                                      I will try to get actual IOP usage today.

                                      @Dashrender said in RAID recommendation for Hyper-V host:

                                      Duh, you're right, my bad.

                                      Though the OP did voice concern about not having any left over storage... So your second solution would solve that.

                                      The idea is to have left over storage for future growth.

                                      Thanks again for all of your input.

                                      JaredBuschJ scottalanmillerS 2 Replies Last reply Reply Quote 0
                                      • JaredBuschJ
                                        JaredBusch @i3
                                        last edited by

                                        @i3 you do not install server 2012 r2 onto the hardware. You install Hyper-V Server 2012 R2

                                        DustinB3403D scottalanmillerS 2 Replies Last reply Reply Quote 5
                                        • DustinB3403D
                                          DustinB3403 @JaredBusch
                                          last edited by

                                          @JaredBusch said in RAID recommendation for Hyper-V host:

                                          @i3 you do not install server 2012 r2 onto the hardware. You install Hyper-V Server 2012 R2

                                          Well he could, but he shouldn't.

                                          1 Reply Last reply Reply Quote 0
                                          • scottalanmillerS
                                            scottalanmiller @JaredBusch
                                            last edited by

                                            @JaredBusch said in RAID recommendation for Hyper-V host:

                                            @i3 you do not install server 2012 r2 onto the hardware. You install Hyper-V Server 2012 R2

                                            This is very important.

                                            I 1 Reply Last reply Reply Quote 1